Hello, I have kind of the same problem; we have PLCs in our cranes, but sometimes they are shutted down. When this happens, after the power is back on, the PLCs won't reconnect to wincc runtime V15.1. We are using S7 Connection and the only way to reconnect the PC is to restart the wincc runtime. I don't see any settings in the TIA Portal that would say "don't reconnect if communication is lost" or "keep conenction even if partner doesn't respond". We have wincc RT Professional (65536) licence active on the server which has wincc runtime on it. Thanks, Gabriel ------------------------------------------------------------------------------------------ |
Last edited by: Moderator_Lan at: 11/28/2024 09:32:38New subject after splitting |
|
11/28/2024 12:10 PM | |
Joined: 7/11/2024 Last visit: 4/16/2025 Posts: 185 Rating:
|
Hello Gabriel I would try installing the latest update as discussed in the other thread. Updates for STEP 7 V15.1 and WinCC V15.1 You should also check that the PG/PC interface is well configured. Also, have you noticed any hardware issue?? Good luck |
If this post has been useful, don't forget to rate it!😊 |
|
1/6/2025 8:57 PM | |
Joined: 9/14/2018 Last visit: 4/8/2025 Posts: 7 Rating:
|
Hello Murof, Happy new year ! Thanks for your answer and yes to all your questions (see printscreen attached). The Softnet licence doesn't look like it's in "use" meaning there's no green arrow next to it. I don't know why it doesn't use it though. Attachment2025-01-06_15-51-46.pdf (63 Downloads) |
1/8/2025 4:58 PM | |
Joined: 9/14/2018 Last visit: 4/8/2025 Posts: 7 Rating:
|
Hello, It turns out installing Simatic Net V15.1 resolved my issue. Thanks all for your help. Attachment2025-01-06_15-51-46_Simatic_Net.pdf (67 Downloads) |