6/24/2013 10:45 AM | |
Posts: 25 Rating: (2) |
of course thank you very much i'll attach some pictures as you can see i have 2 on/off switches and 2 potentiometers i was thinking to use the switches as start stop buttons and the potentiometres : one to set the reference and one to simulate the signal receved from a flow transducer Attachmentlevel.zip (389 Downloads) |
Last edited by: bbc91 at: 6/24/2013 10:45 AM |
|
6/24/2013 11:01 AM | |
Joined: 3/18/2008 Last visit: 12/8/2023 Posts: 1750 Rating: (270) |
Hello, As you mentioned in the Subject , Software is Step7 V5.5. Hence you need FB41 PID Block from Standard Library of Step7. You have to Call this Block in Cyclic interrupt OB35. Also have a look a following Threads. PID Controller PID in Step7 Hope this helps... |
VANDE MATARAM..... |
|
This contribution was helpful to2 thankful Users |
6/24/2013 11:22 AM | |
Posts: 515 Rating: (56) |
HI, Find an attached example. Use it as you reference. You can find the FB41 block inside the libraries-standard library-pid control blocks. assign the parameters as mentioned in the example attached. give the desired setpoint in the 'SP_INT', assign the input from your potentiometer to 'PV_PER' (if you are feeding it directly through the AI card or else if you are using the scaled value rather than directly feeding through the AI card, use 'PV_IN' instead. Assign the tuning values as required (P & I value). For more help you can click on the block and F1. First try it in manual mode and c whether you are getting the output and then go for the auto mode
AttachmentPID BLOCK.pdf (499 Downloads) |
This contribution was helpful to1 thankful Users |
6/25/2013 7:46 AM | |
Joined: 1/28/2009 Last visit: 4/1/2024 Posts: 6836 Rating: (1359)
|
Hello, I guess you want to implement a cascade control structure with FB41.Please read the following topic: Need help in Cascade control method... Best regards Hamid Hosseini |
This contribution was helpful to3 thankful Users |
6/25/2013 9:44 AM | |
Posts: 25 Rating: (2) |
thank youhdhosseiniyou've been very helpfull ! |
This contribution was helpful to1 thankful Users |
6/25/2013 10:32 AM | |
Joined: 1/28/2009 Last visit: 4/1/2024 Posts: 6836 Rating: (1359)
|
Thank you bbc91 for your feedback. For cases related to PID controllers we have huge collection of interesting topics.All topics related to PID controllers and mainly FB41 can be searched via " "STEP7 Additional Software" " conference.
Best regards Hamid Hosseini |
7/3/2013 6:56 PM | |
Joined: 3/18/2008 Last visit: 12/8/2023 Posts: 1750 Rating: (270) |
Hello, I have gone through your codes and i found memory overlapping which i have resolved. In OB35 , there is a PID Block in which following are the addresses SP:MD 90 PV : MD 220 LMN Controller OUTPUT:MD 110 CP 343-1 IP Address 192.168.0.1 Sub net mask 255.255.255.0 PC IP Address 192.168.0.2 Sub net mask 255.255.255.0 Checked the attached Program for reference. Hope this helps. AttachmentPrograms.zip (291 Downloads) |