Please, could you explaing what this error means and what should I do? I have a profibus DP network commanded by a s7300. I have a ET200S faulting randomly: the SF led flash 3 times then the BF led do it 8 times, continously. There are no I/O faulted. Thanks. AttachmentDiagnose0041.txt (131 Downloads) |
10/4/2017 10:03 AM | |
Posts: 1368 Rating: (128) |
Hello, The information about the cause of the problem is determined by means of the LED fault display. After an announcement by means of a flashing signal, the respective error type and after that the error location / error code are displayed. LED:SF ==> Announcement of error type LED:BF ==> error type I do not know, which IM you use, you find more information about error coding in manual of IM e.g.https://support.industry.siemens.com/cs/ww/de/view/35363377/en?dl=en Please have a look in the manual of you IM to find out the error... Are there repeaters in the network? Are they okay? ...have also look on this post https://support.industry.siemens.com/tf/ww/en/posts/sf-bf/178057/?page=0&pageSize=10 |