Dear mhkocak, before switching ON you need to activate the pol-ID (p1982) and chose a suitable method (p1980). If motor manufacturer does not specify a certain method you need to try which one gives you best results and which is working with your application...(is motion allowed or not,...) r1992 of expert list gives you a status of current pol-ID. Further info is given in Function manual S120: https://support.industry.siemens.com/cs/ww/en/view/109754299 Chapter 4.13 ff Hope this helps! |
With best regards, |
|
This contribution was helpful to2 thankful Users |
5/22/2018 5:39 PM | |
Joined: 1/8/2009 Last visit: 6/5/2024 Posts: 43 Rating: (0) |
Thank you TechTeam, The new manual linked by you has more information and details. |