1 thankful Users |
5/22/2019 11:12 PM | |
Joined: 9/27/2006 Last visit: 3/18/2025 Posts: 12344 Rating:
|
Hello Mathieu; Your last post is a bit confusing. Is it correct that you would like to communicate with 6 FC302 drives using Modbus RTU? First point: you can use either a CM 1241 (RS-485) or a CB 1241 RS-485 with your CPU 1215C, so you have a choice, even if you are using an encoder card: How do you establish a MODBUS-RTU communication with STEP 7 (TIA Portal) for the SIMATIC S7-1200? https://support.industry.siemens.com/cs/ww/en/view/47756141 You can install one CB in your S7-1215C, and 3 CMs. You will be able to find the differences between a CM 1241 and a CB 1241 in the Appendixes of the S7-1200 System Manual: https://support.industry.siemens.com/cs/ww/en/view/91696622 Second point: with a RS-485 comm module or board you can communicate with multiple Modbus slaves, using the Modbus RTU instructions of the S7-1200.Look at this discussion, it might answer most of your questions on multiple FC 302 drive connections: Hope this helps, Daniel Chartier |