In ET200S How many DI,DO,AI,AO can be connected with One Power Module. |
7/9/2015 2:38 PM | |
Joined: 8/31/2013 Last visit: 4/3/2023 Posts: 592 Rating:
|
You can know How many DI,DO,AI,AO from the Hardware configuration it self |
Warm Regards |
|
7/9/2015 3:13 PM | |
Joined: 8/31/2005 Last visit: 4/24/2023 Posts: 2194 Rating:
|
Add the currents you can find in the technical data for each module. This must be lower than the max. current of the power supply. Or use the TIA Selection Tool to configure your station. As I know, It does the same and will notice you when a additional power supply is needed. |
|
|
3/4/2016 11:36 AM | |||||||||||||||||||||||||||||||||||||
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating:
|
hi Rakesh, the power-consumption of is for all currents that go out of the system. If you use the supply from the switches, sensors and buttons are from the Terminal-Modules of the ET200s- DI´s you need the input-current for "1"-Signal. that is typically 5mA. This is so low, that you normally only calculate with the Output-current of the DO-Modules.
6ES7131-4BF00-0AA0hope this helps, regards, |
||||||||||||||||||||||||||||||||||||