Hello, Well, you have to calculate the total power requirements of the system, usually i supply outputs with a seperate supply( inductive loads like pneumatic valves) ,you don't want the cpu to go down because of a faillure in 1 single output, PFC=Power Factor Correction, you can reed about that here : http://power-topics.blogspot.com/2008/02/what-is-pfc-and-why-do-i-need-it.html Regards, Marcjan |
Last edited by: Marcjan at: 11/30/2011 7:48 AMProblem solved? |
|
11/30/2011 8:04 AM | |
Joined: 3/21/2006 Last visit: 7/12/2023 Posts: 10221 Rating:
|
Hello, Yes, you can use it. The difference between both is limiting supply harmonics with 6EP1333-2BA01. Take a look for comparing at https://eb.automation.siemens.com/goos/catalog/Pages/ProductData.aspx?catalogRegion=WW&language=en&nodeid=10029628&tree=CatalogTree®ionUrl=/#A&activetab=product& It might be useful - http://support.automation.siemens.com/WW/view/en/54418102 Best regards, Hristo MIhalev |