12/14/2023 8:11 PM | |
Joined: 12/18/2014 Last visit: 1/13/2025 Posts: 34482 Rating: (4304)
|
Which LOGO! BM have you? With relay outputs or transistor outputs? Which load will you switch with the outputs? |
12/14/2023 8:18 PM | |
Posts: 5 Rating: (0) |
logo 6ED1052 2MD08-0BA1 12/24RCEo DM 16 relays the relays will be used for switching another relays, from Finder, so low current use for lighting in a building |
12/14/2023 8:53 PM | |
Joined: 12/18/2014 Last visit: 1/13/2025 Posts: 34482 Rating: (4304)
|
Then must you calculate with the load currents ... |
12/15/2023 9:44 AM | |
Posts: 5 Rating: (0) |
fuses will be used for safety, that is clear, so calculating currents: 165 mA for the BM 8 x 2 dm16's x 2 mA is 32 mA total 197 mA . but in this link logo! dm16 24r current is 30 ..115 mA: that is much higher. AttachmentLOGO_EM_PI_V8.4_20230316.pdf (473 Downloads) |
Last edited by: The Helping Hand at: 12/15/2023 10:05:29Text formatting optimized and PDF-File attached from Link |
|
12/15/2023 7:58 PM | |
Posts: 5 Rating: (0) |
thanks for the answers |