9/21/2012 8:41 PM | |
Joined: 9/27/2006 Last visit: 3/27/2025 Posts: 12344 Rating:
|
Hello Mr. G. First question: does your A-B PLC have a Profibus-DP master communication processsor in the rack at this time? If not, here are products from the 2 major Encompass vendors for these comm processors: http://www.molex.com/molex/products/family?key=brad_sst_communication_modules_for_rockwell_automation_pac__plc_controllers&channel=products&chanName=family&pageTitle=Introduction http://www.prosoft-technology.com/prosoft/products/for_rockwell_automation/protocol/fieldbus_automation/profibus_dp Both vendors produce excellent material, and accompany their processors with sample code to be integrated in the PLC prograam and a Profibus-DP configurator that wil allow the slaves o be mapped. if there already is a Profibus-DP master interface, make sure you ahve access to the Profibs configurator so you can untegrte the slaves. Second question: do the probes have a Profibus-DP slave channel integrated in their electronics, or will you have to use a Profibus-DP remote I/O staton. An ET 200M station for examples uses S7-300 i/o modules hooked up to a IM 153-1 or -2, and you can connect the slave\s analog output to an analog input module on the ET 200M to bring the signals to the PLC over Profibus. There are many pending details to discuss, but I will wait for your answers in order to have an idea of what you are planning to do. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 9/21/2012 8:42 PM |
|