Hello, I wrote a program to verify that: The retentive data will be initialized after a cold restart is performed. During the experiment I’ve encountered a problem: When I chose to download ‘All’ to device to perform a cold restart , the retentive data: “Data_block_1.shu” could not be initialized. And if I chose to download “Hardware configuration” to device , the “Data_block_1.shu” was initialized.
AttachmentScreenshots.pdf (662 Downloads) |
Last edited by: anxiao at: 11/9/2011 11:38 AM |
|
11/29/2011 3:36 PM | |
Joined: 10/10/2005 Last visit: 1/29/2025 Posts: 1940 Rating:
|
Hello, it is a different, whether you declare a new DB as "Optimezed" or as "Standard-compatible with S7-300/400" in the Add new block dialog. By optimezed DBs you can choose for each single DB variable whether do you want with "Retain" or not. Perhaps the following FAQ could be mainful for you: http://support.automation.siemens.com/WW/view/de/50697467 With best regards |