11/9/2011 11:36 AM | |
Posts: 7 Rating: (1) |
Hello, I'v encountered the following problem:PG is connected to CPU315-2 PN/DP via Ethernet.The CPU315-2 PN/DP is connected to Sinamics S120 with CU320 via Profibus.When I'v tried to connect Scout to do some changes to inverter, connection could not be established.I could download the HW configuration and NetPro configuration to the CPU, and there is not fault on BF. The hardware: CPU 315-2 PN/DP 6ES7315-2EH13-0AB0 V2.5 CU320: 6SL3040-0MA00-0AA1 CF card: 6SL3054-0CE01-1AA0 performance 1 V2.4.1.6 The Software: Step 7 V5.5 Scout: V4.2. sp1 Someone said this should be a problem with SIMATIC CPU. How to solve it. AttachmentScreenshots.pdf (112 Downloads) |
11/9/2011 2:16 PM | |
Joined: 4/24/2006 Last visit: 9/23/2024 Posts: 8742 Rating: (1168) |
Hello anxiao, Did you in Netpro perform a download to CPU315-2PN/DP (Download selected stations) Best regards, Wizard |
11/10/2011 11:18 AM | |
Joined: 4/24/2006 Last visit: 9/23/2024 Posts: 8742 Rating: (1168) |
Hello, I guess you have seen this link: http://support.automation.siemens.com/WW/view/en/22794082 Perhaps this link: What do I have to consider establishing a routed connection with the new SINAMICS G120 Generation? Here you can download latest firmware of CPU: Operating System Updates for CPU 315-2 PN/DP (6ES7315-2EH14-0AB0) So you should use another CPU315-2PN/DP (2EH14) Best regards, Wizard |
Last edited by: Wizard at: 11/10/2011 11:25 AMLast edited by: Wizard at: 11/10/2011 11:22 AMfirmware CPU |
|