7/15/2012 9:32 AM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating:
|
Hello, There is an FAQ with the most common DIP settings: http://support.automation.siemens.com/WW/view/en/50837578 I just wonder about the type of fiber used. SM G652D I looked on Internet, and all links are refering to G652 as being a single mode fiber. An example: http://thefoa.org/tech/smf.htm G652 is here the name of an ITU standard and does npt refer to the fiber core62.5 micrometer. The G652standard specifies fibersoptimized for 1310 nanometer light. The OLMG11 (6GK1503-2CB00)is intended to be used with Multimode fiber and 850 nanometer light as specified by the technical data here: http://support.automation.siemens.com/WW/view/en/25307618/td In my opinion, wrong fiber type ...for that OLM type. |
Best regards |
|
7/16/2012 9:06 AM | |
Joined: 2/5/2011 Last visit: 4/6/2024 Posts: 90 Rating:
|
hello shall i change the bus parameters in network setting(ex:time slot,...)? |
Last edited by: ACDC24 at: 7/18/2012 8:49 PM |
|
7/18/2012 2:37 PM | |
Posts: 1547 Rating:
|
Hello ACDC24 Youmust not change the hw config. What is with the measurement? |
7/19/2012 3:03 PM | |
Posts: 1547 Rating:
|
Hello ACDC24 look at the Manual at Page 43. What is the received value? |