Hi hueng, Is there more than one PG port on the PLC? If so, you should use SI1 (the 'deepest' one) Kind regards, BV |
4/12/2012 10:32 AM | |
Joined: 7/18/2011 Last visit: 10/9/2023 Posts: 521 Rating: (91) |
Hi hueng, There appear to be some special requirements to connect a PG. Please check out section 10.18 of this manual. Kind regards, BV |
4/12/2012 8:13 PM | |
Joined: 4/5/2006 Last visit: 8/13/2023 Posts: 642 Rating: (131) |
Hello, you need the original cable for a PG or a cable with separate power supply because the 115F not provides the voltage for the cable. Regards André Räppel --------------------------------------------------------------------------------- www.raeppel.de