Hi all, I tried to transfer 100 real values between three controllers using GET/PUT Instruction (S7 1500, s7 400 & IM 151-8). Communication is established but cant able to transfer more than 50 values from/to IM 151-8. Between s7 400 to s7 1500,transfer of 100 real values is happened but cant with third controller. here with i attached the program backup. Can you please help me to sort it out. Next i am going to try with four controllers (S7 1200) using router, Need suggestion for that too. Thanks in advance AttachmentGET PUT_Three Controller.zip (39 Downloads) |
1/21/2018 5:12 AM | |
Joined: 10/7/2005 Last visit: 3/20/2025 Posts: 3042 Rating:
|
Hello Ashu009 you are reaching the limit of what is possible with GET/PUT in an S7-300 (IM151-8 is part of the 300 family too). 160 Bytes is generally the limit (albeit some 300's may allow a few Bytes more) and please see What-properties-advantages-and-special-features-does-the-s7-protocol-offer? for more on this. The same applies to S7-1200, so you need to use either BSEND/BRCV or implement a Multiplexer as per Siemens example for S7-300 and S7-1200 |