3/3/2013 5:30 PM | |
Joined: 3/21/2006 Last visit: 3/19/2025 Posts: 10239 Rating:
|
Check it there - How do you parameterize the communication resources of S7-300 CPUs so that WinCC stations and S7-300 stations do not have connection failures? Best regards, Hristo Mihalev |
3/4/2013 10:36 AM | |
Posts: 13 Rating:
|
Thanks Mr/ Hristo MiIhalev , I already enabled 2nd PC station in the hardware configuration and the paramters of address details, connections and hardware configuration are attached with a thread Must I reconfigure the OP communication to be 2 or not ? Best regards, Fouad AttachmentAttachments.zip (259 Downloads) |
3/5/2013 10:49 AM | |
Posts: 13 Rating:
|
Dear all experts : please any one reply to me Best regards M.Fouad
|
3/5/2013 3:03 PM | |
Joined: 3/21/2006 Last visit: 3/19/2025 Posts: 10239 Rating:
|
You can increase the numbers of S7 connection (put 5 there) not OP connections. More info at -http://support.automation.siemens.com/WW/view/en/22276718 I sugest you instead of using Simatic Net Server to use DASISIDIRECT Server. The parametization is much easier there. Search for 'DASSIDIRECT' or I can send you manual too... Best regards, Hristo Mihalev
|
3/5/2013 3:58 PM | |
Posts: 13 Rating:
|
Thanks so much ; I have already used the DASSDIRECT notSimatic Net Server , By the idea ; I can't edit the S7 communication because it is configured automatically according to PCs stations that added in the hardware configuration please see the attached image Attachments7 communication.zip (283 Downloads) |