Hello Ashu009 Runtime Settings-> OPC Settings -> configuration of OPC UA Server.... The OPC UA Server is always running if you start the Runtime. Look at this here is everything explained: https://support.industry.siemens.com/cs/ww/en/view/109755215 By Murof |
If this Information really helps, you could use the Rate function |
|
This contribution was helpful to
2 thankful Users |
6/8/2018 4:19 PM | |
Joined: 9/5/2017 Last visit: 4/22/2025 Posts: 21 Rating:
|
HI Murof, Now i am getting connection with opc client, but cant able to get tags from wincc. after installing simatic.net the connection established. Is there any option for wincc Like "allow access to opc(in plc)" .
|
Last edited by: Ashu009 at: 6/8/2018 4:20:59 PM |
|
6/15/2018 2:35 PM | |
Joined: 8/3/2009 Last visit: 4/17/2025 Posts: 15311 Rating:
|
Hello Ashu009 You have to manage the OPC Certificates exchange. For an Example have a look at this FAQ there is a WInCC Professional RT as OPC UA Server: https://support.industry.siemens.com/cs/de/en/view/63481236 Or this one: https://support.industry.siemens.com/cs/ww/en/view/109479664 Bye Murof |