4/12/2019 12:34 PM | |
Joined: 7/25/2017 Last visit: 5/5/2024 Posts: 297 Rating: (44) |
Hi Robbe, In your previous post (https://support.industry.siemens.com/tf/us/en/posts/plc-and-sinamics-s110-profinet/210046/?page=0&pageSize=10) you said that it runs from Starter, but in this post you said it doesn't. I'll assume it doesn't. I don't have a S110 system I can test with, but something like the attached should hopefully work? Simple configuration: no extra function modules, Telegram 3 selected. I believe you only have telegram 3 available for S7-1200 TO positioning. You must get it running from Starter (control panel) before moving on to TIA Portal. On the TIA Portal side, you don't need topology and I'd suggest removing it. It's not advantageous for S7-1200 control. You just need the S110 device networked with correct IP, Profinet name and telegrams, then map the telegrams to a TO configured for Profidrive. Just set up the Drive and Encoder sections of the TO, nothing else, then try to run it from the control panel. If you can do this then save the projects; it is your fallback point in case something goes wrong later. I've attached a sample project in V13 SP1 because I don't have V14 w/o SP. Hope that helps. AttachmentS110.zip (81 Downloads) |