Dear all, I want to communicate CPU 313C-2DP and CPU 315-2DP over Profibus communication. I configured CPU 313C as DP-Slave and 315 as DP master. but after both CPUs hardware configuration when I put them run mode then system Fault shows and both CPU goes into stop mode. I am attaching the Diagnostic Buffer file of CPU. Please Help me.... regards, darsh
AttachmentDianose.zip (148 Downloads) |
8/2/2011 11:36 AM | |
Joined: 8/31/2010 Last visit: 9/18/2024 Posts: 1521 Rating: (227) |
This will be helpful. Check it out. How do you configure an S7-300 CPU as DP slave to a CP 342-5 as DP master? |
Like it? Rate it! |
|
8/2/2011 11:42 AM | |
Joined: 1/28/2009 Last visit: 9/10/2024 Posts: 6849 Rating: (1365) |
Hi Check the steps described in this example as an illustration of how configure 2 S7 stations one as a master and the other as an Slave. DP link between CPU 315-2DP (slave) and S7-400 (master) with STEP 7 V5.3 Regards |
8/2/2011 11:46 AM | |
Joined: 3/21/2006 Last visit: 9/10/2024 Posts: 10228 Rating: (1181) |
Hello, Download OB82 in CPU. Attach here hardware confuguration. Best regards, Hristo MIhalev |
8/3/2011 6:19 AM | |
Joined: 12/3/2010 Last visit: 9/5/2024 Posts: 31 Rating: (1) |
DearUMENCHO, here is the PLC Hardware Configuration you required. downloading OB83 solved my prolem .but can u explain me how. and I m too getting two warning in NetPro. take a look. Regards, Darsh AttachmentProfiComm.zip (168 Downloads) |
Last edited by: darsh at: 8/3/2011 6:20 AMsorry, downloading OB82 solved my problem |
|