Posts: 14 Rating: (0) |
After AI you must connect Analog amplifier block.In parameters menu select type of sensor (Pt100 in your case) |
12/27/2013 8:57 AM | |
Posts: 13 Rating: (0) |
Thank you very much! Problem solved! One amplifier was configured as "no sensor"
|
This contribution was helpful to1 thankful Users |