4/16/2014 4:58 PM | |
Posts: 6 Rating: (0) |
I had a problem with analog input card(6ES7331-7NF00-0AB0). All channels on this card are conected on PT100 sensor and they are calibrated. During the calibration on this month the technical found differences at calibration points. The the sensors are mensuring 3.5°C than standard. To solve the problem I replaced the card with a new. I would like to know, if anyone have idea what can cause this problem, for me ensure that this problem doesn't happen in others racks. Thanks. Best Regards. |
4/17/2014 6:08 PM | |
Posts: 96 Rating: (7) |
The module no. you have posted does not measure RTDs ( PT100 ); |
4/17/2014 6:21 PM | |
Posts: 6 Rating: (0) |
Hi Raednabeel, The hardware channels are configured to read 4-20mA.Do you know what can cause the problem at the module? Best regards, M.Fernandes
|