10/7/2016 1:40 PM | |
Joined: 10/26/2011 Last visit: 5/14/2024 Posts: 761 Rating: (190)
|
That is a system behavior. The opening of the selected Faceplate (SelFp) is a one way function. If you want a jump back, you have to engineer the same for the FB200. Here an abstract from the APL manual: "From the standard view and from the preview, you can use a button to open the standard view of a block that can be selected freely. In order to use this function, in the CFC you need to interconnect theSelFp1input parameter for the button in the standard view orSelFp2for the button in the preview to any given output parameter of the block whose faceplate is to be opened. This makes the buttons in the faceplates visible." SIMATIC Process Control System PCS 7 Advanced Process Library (V8.2 SP1) |
Last edited by: Thunderstorm at: 10/7/2016 1:51:29 PMSIMATIC PCS 7 - Overview |
|
This contribution was helpful to1 thankful Users |
10/7/2016 2:04 PM | |
Joined: 12/23/2011 Last visit: 11/22/2022 Posts: 143 Rating: (0) |
very thanks. Yoursayis correct.
|
10/7/2016 2:04 PM | |
Joined: 12/23/2011 Last visit: 11/22/2022 Posts: 143 Rating: (0) |
|
Last edited by: PLC2011 at: 10/7/2016 2:05:28 PM |
|
10/13/2016 2:06 PM | |
Joined: 12/23/2011 Last visit: 11/22/2022 Posts: 143 Rating: (0) |
hi yes i check internal tag and i see created the variable xxx.SelFp1#Jump |
10/14/2016 8:01 PM | |
Joined: 12/23/2011 Last visit: 11/22/2022 Posts: 143 Rating: (0) |
the pictures |
Last edited by: PLC2011 at: 10/14/2016 8:02:37 PM |
|
10/14/2016 8:03 PM | |
Joined: 12/23/2011 Last visit: 11/22/2022 Posts: 143 Rating: (0) |
|