Hello, here the corrected project. 1.) HWCfg error: on compile you get the message that HWcfg can't be compile, so i have open HWcfg and compile. Here the message "object not found" occurrs, i have check i the adress view in HWcfg for non used slots and found that's a adressslot with adress 256 is exist but not used or seen in the devices. So i have reorg the adress data with the key combination CTRL+ALT+F11, the it works. 2.) Project: three things are bad. You haven't enable the LineModule so the drives get no enable bit to start, i have insert a Unit CTRLAlm to do this. Second problem is that you use the BackgroundTask for the Motion commands. The Background is a cyclic system Task and can't use motion commands which have a blocked call. You enableAxis have set the option "When_command_done" activated for the program execution so the task is blocked until the command is done, some on the pos command, here you use the option "when_motion_done". booth settings can cause a overflow of the backgroundcycle so better way is you use motion tasks. I have put your program to a motiontask and start this task from the ctrlalm program which is automaticaly start when CPU go to RUN. Third problem ist the faultTask. You have no programs for the system fault tasks, so everytime the system have a fault from technology or peripherie the PLC go to STOP, i have insert a litte program for the faulttasks. Regards Christoph AttachmentD:\sIMOTION.zip (108 Downloads) |
8/14/2014 11:47 AM | |
Posts: 55 Rating: (0) |
Hi Chris, The first many many thank you correct and fixed fault help me. i continous get one problem about control panel commisioning. when i do control panel for quickly commisoning Servo, it show error with attached file " The Switch-on disable of the infeed is active!!'. what can i do for truble it. Thank You! AttachmentDisable infeed is active.zip (95 Downloads) |
8/15/2014 6:54 AM | |
Posts: 55 Rating: (0) |
Hi Chris, i am doing commissioning via control panel. Still have problem "The switch-on disable of the infeed is active!". i can not fixed now Step by step i did as bellow: 1. Go online accessible nodes. 2. Accept Unit Drive to Project. 3. Automactic Congiguration. 4. Download project to HW. 5. i got one warning attached file "Warning.PNG" 6. I go SERVO_03 then do Commissioning Control Panel. 7. I do "Assume Control Priority". 8. Click button "LM BOX". 9. it is pop up message box "The switch-on disable of the infeed is active!" attached file MSBox.png. i can not run Drive Servo_03 by commisioning control panel. Please help me what can i missing? Please help me as you can. i am commisioning for Project urgently. i am doing with PC have teamview: ID: 861 420 628 Pass:546qvc P/S: much appreciated your support AttachmentInfeed Active (Smart line module).zip (97 Downloads) |
8/18/2014 6:20 AM | |
Joined: 5/12/2006 Last visit: 5/14/2024 Posts: 22251 Rating: (2985)
|
Hello, check the state of the line Module in the Diagnostic overwiew. Regards Christoph |
8/18/2014 6:53 AM | |
Posts: 55 Rating: (0) |
Hi Chris, Diagnostic forLine Module only show attached file. i can not find problem to fix it. Do you have advice? thisfault take me a long time pause project. please help me. Thank you!
AttachmentAlarm infeed.zip (98 Downloads) |
8/18/2014 6:58 AM | |
Joined: 5/12/2006 Last visit: 5/14/2024 Posts: 22251 Rating: (2985)
|
Hello, i mean the window diahgnostic Overwiev (th last tab in the detail windows). Regards Christoph |
8/18/2014 8:31 AM | |
Posts: 55 Rating: (0) |
Hi Chris, This photos diagnosics ovievew. please givethe advice. thank you!
AttachmentDiagnotics.zip (92 Downloads) |
8/18/2014 10:41 AM | |
Joined: 5/12/2006 Last visit: 5/14/2024 Posts: 22251 Rating: (2985)
|
Hello, is no goodidea to connect the 3AC 400V power directly to the LineModule without a filter. Readthe manual for the correct line connection. You can't move or pos the axis without a correct working line module. Regards Christoph |
8/18/2014 10:56 AM | |
Posts: 55 Rating: (0) |
Hi Chris,Total agree with you!
|
8/19/2014 9:32 AM | |
Posts: 55 Rating: (0) |
Hi Chris After put in the filter, the infeed looked OK However, once we use a simple logic to control the motor the fault come up as picture attacheed We also attached the logic as well. Can you please help us find why the fault happen? Thank you very much
Attachmentattached.zip (78 Downloads) |
8/21/2014 10:57 AM | |
Posts: 55 Rating: (0) |
Hi Chirstoph, System SIMOTION C240 control S120 CU320 2 DP with module power servo03/04 my objective: how i can Sevor_03 Homing at 10deg ( or expect positon when comisioning) by Push button on HMI. that mean,before do process, operator must press Push button Home on HMI or PB home hardware. As Operator pressed Push button HOME on HMI, servo will go HOME at 10deg (HOMED) or expect position when commisioning. How to do on Axis Homing of C240. do we need Proximity Sensor wiring to C240 to detected HOMED? please give me your advice. Please take a look attached file help me! Much appriciated!
Attachmenthome.zip (110 Downloads) |