Hi everyone, I'm trying to install a DP/DP Coupler in my PROFIBUS master system but, when I download the configuration of the hardware the PLC enters in System Failure. I don't have Bus Fault, which means that, the two equipments can communicate with eachother, but I can't solve the problem with the SF Led. I have some Errors in the Module Information. The PLC that I'm using is CPU 317-2 DP firmware version 2.6 and the DP/DP Coupler is 158-0AD01-0XA0 firmware version 3.0.2. Thank you, João Martins AttachmentHardware.zip (92 Downloads) |
4/14/2020 5:23 PM | |
Joined: 9/27/2006 Last visit: 6/3/2023 Posts: 12033 Rating:
|
Hello Jmartins; And where is the second Profibus master, with its own Profibus configuratipon? The DP/DP coupler will not become active until is receives a connection from both masters. Have a look at the screenshot below, taken from the DP/DP coupler manual: https://support.industry.siemens.com/cs/ww/en/view/1179382 Hope this helps, Daniel Chartier |
4/15/2020 10:19 AM | |
Posts: 13 Rating:
|
Hello Daniel, I guess I have all the attachments that you asked for. I set the profibus addresses for each slave on the dipswitches that I have in the DP/DP Coupler. And the addresses correspond to the ones that I have in the HW configuration. Thank you for the help, João Martins AttachmentDPDP_Coupler.zip (121 Downloads) |
4/15/2020 2:03 PM | |
Posts: 13 Rating:
|
Hello Daniel, Here it is the screenshots that you asked for, I think. Thank you, João Martins AttachmentSlave2.zip (103 Downloads) |
4/15/2020 3:36 PM | |
Posts: 13 Rating:
|
Hello Daniel Here it is what you asked for. Thank you, João Martins AttachmentSlave1.zip (90 Downloads) |