10/23/2018 5:41 PM | |
Joined: 3/28/2010 Last visit: 12/5/2024 Posts: 1094 Rating: (215) |
Current output needs to be enabled on the Mass 6000 under current output in the menu. I'm not sure the factory default is disabled, but I've run into a number of them that are disabled. The Ex-d version Mass 6000 has an active/passive selection (output powered by the flow meter [active] or powered by an external power supply [passive]). https://i.postimg.cc/pLBQfc0p/Mass-6000-Ex-d-version-passive-or-active-4-20m-A-jumper.jpg I do not know whether the non-Ex-d versions have the same active/passive jumper choice or not. If passive is selected, you won't get any current output until an external DC power supply powers the loop. |
10/24/2018 5:56 PM | |
Joined: 10/2/2017 Last visit: 11/27/2024 Posts: 25 Rating: (0) |
I can say that output signal 4-20mA is active in the settings. I checked it out a few times. All settings are okay. |