2/29/2012 8:40 PM | |
Posts: 2 Rating: (0) |
Hi, I have same problem with my 1214C, V2.2 and TIA 11 sp2. When I download prepared project (from my college, he has the same version of TIA and windows 7 32bit) to CPU, evrything goes well and I´m able to watch every block in oline mode. BUT, if I change something in this block, compile and upload to cpu, the TIA show me block as a different in offline and online. When I compare off/online, there is no different between them. If I try to upload data back form CPU to my pc, it is not possible, because TIA gets down and show error message (internal tia message and after that the windows message about non responding program). The same problem is when I create new project in my pc and upload this to cpu. The data in cpu shows different. I´ll be thankful for any idea to solve this problem ! |
Last edited by: O_Moderator at: 3/1/2012 9:28 AMnew subject after splitting from /tf/WW/de/Posts/53899#top |
|
2/29/2012 10:27 PM | |
Joined: 8/25/2005 Last visit: 10/5/2024 Posts: 1162 Rating: (111) |
Hi, have you seen the following discussion: Problems downloading new code to S7-1200 So please try to change the date to another one than 02/29 Good luck Sabine |
3/1/2012 6:42 AM | |
Posts: 2 Rating: (0) |
Tahnk you very much. It works ! Something is wrong in Siemens, I lost whole day and half of my hair... |