7/18/2016 9:12 PM | |
Posts: 4 Rating:
|
hi comunity; i have a small problem with my PLC S7 1200 1211c v1.0. with this PLC its imposibel to conect on the network profinet with ET200S. I create the profinet sub net and connect both device and the controle io is not assigned to ET200s. which is the problem? in this link they can see the problem: frimware 1.0 http://giphy.com/gifs/3o7TKsqSdPQLME85os with other version of firmware in the same PLC dont happens this, with other version 2.0 happen this: What I can do? I can only solve this by updating the software? |
7/18/2016 10:30 PM | |
Joined: 7/7/2010 Last visit: 3/26/2025 Posts: 15762 Rating:
|
1. Get S7-1200 compatible MMC (you probably have one already). 2. Install firmware version 2.2 onto that MMC. 3. Upgrade your S7-1200 to V2.2 of firmware. 4. Change your project to reflect V2.2 of the PLC firmware. Maybe this will work, but it is not likely.
|
science guy |
|
This contribution was helpful to
1 thankful Users |
7/19/2016 8:30 AM | |
Joined: 9/29/2015 Last visit: 3/6/2023 Posts: 63 Rating:
|
Hi enrialanso, Have you assigned the device name, click on the IO-Device, click on Properties Tag at below of that screen, there is a tab called ethernet adresses, there you would see the converted name. I put the screenshot on the message. Copy that converted name and find the device by ethernet, assign it to the device, than try again to go online. Hope That Helps |