11/27/2009 9:18 AM | |
Posts: 23 Rating:
Hello, I have a problem with old 313C CPU digital inputs (DI) modules states. The situation from the beginning is: 313C with its own I/O 3 modules x16 inputs 2 modules x16 outputs PLC firmware is 0.0 (about 2001 years) Now we added two modules: 32 DI and 32 DO after these 5 modules. The configuration is: 2. CPU 313C 3. IM365 4. DIx16 5. DIx16 6. DIx16 7. DOx16 8. DOx16 9. DIx32 10. DOx32 In the module of 32 DI, when I come online, i see only the first byte correctly as inputs are really TRUE or FALSE, but there is a problem with other inputs. Byte 2 is the "mirror" of module 5 (DIx16) second byte. Bytes 3 and 4 I dont see at all (I see them FALSES). When I disconnect the front connector of module 5 - the seconds byte inputs of module 9 also goes to FALSE. First of all I though maybe there is a problem with 32DI module. I tried the only 32DI near the CPU - all inputs i could see as they are. Then I changed the configuration - put 32DI near CPU 2. CPU 313C 3. IM365 4. DIx32 5. DIx16 6. DIx16 7. DIx16 8. DOx16 9. DOx16 10. DOx32 The problem now is: When i come online, second byte of module 7 is the "mirror" of second byte of module 6. When I disconnect the front connector of module 6 - the seconds byte inputs of module 7 also goes to FALSE. There is no address ovelapping in hardware configuration and this is not my first siemens plc, so there is no stupid mistakes. It is some anomaly.. I attached the online view of 32DI (when it was module 9) and module 5 (16DI) AttachmentDI_states.zip (19 Downloads) |
11/27/2009 10:15 PM | |
Joined: 5/28/2008 Last visit: 10/2/2023 Posts: 4477 Rating:
Dear Arvydas, Please let us know if you are using more than one power supply in your system? If so, can you tell in if these two power supplies are comon ground or not or how did you connect them? Also let us know the part number of the twi DI modules you use (32 & 16) DI modules. And please check that you have connected the (M) of the power supply to (M) of each module you have selected. If you have more than one power supply, one of them feeds sensors or limit switches or whatever connected to one of these modules. check that the (M) of the DI module is connected to the (M) of the power supply which feeds the sensor or limit switch. Waiting for your feed back. Regards, |
Ayman Elotaify |
11/28/2009 10:11 PM | |
Dear Arvydas, Really strange problem! May be something wrong in the modules. Let's try another thing. What will happen if you put only two modules in slots 4 & 5. And do not connect the field to DI channels. Only (M) to the modules should be connected. Then try each DI channel and see what will happen. Then disconnect the front connectors and install other two modules and so on.
How did you know that the DI should be true? You said diod is On. Did you meant the led of the DI channel is lit and it is False in Variable table? If so, Please measur the Voltage on this channel using a multmeter. If the voltage is lower than 13VDC, The led is lightlly lit but the DI is False. Please see the attached picture from the manual. Regards, |