4/3/2012 10:37 AM | |
Joined: 8/31/2005 Last visit: 1/20/2025 Posts: 2198 Rating:
|
This seems to be ok, but what about the other +V and 0V wire? Check the 12V output is not overloaded. Make shure A and B show more than 12V (against ground and 0V) as high signal. (You can use a normal (digital) voltage meter, just turn the encoder slowly until you have a high signal) According to the attachment, I'm not shure the encoders "XCC 15......Y" give enough voltage to the outputs (additional note: RS422 - 5 V.) Maybe you need the 1Count5V Attachment169001701A55.pdf (240 Downloads) |
|
|
4/3/2012 11:25 AM | |
Posts: 45 Rating:
|
hello, i make the measurements A and B against 0V and i have 22V. thanks for your cooperation, best regards, myhay ene |
4/5/2012 1:12 PM | |
Joined: 8/31/2005 Last visit: 1/20/2025 Posts: 2198 Rating:
|
Well, the manual says to the terminal modules:
|
|
|