9/5/2016 9:36 PM | |
Posts: 6 Rating: (0) |
attached the PLC ING page and some other pic and microwin program .wish it can help. |
This contribution was helpful to1 thankful Users |
9/5/2016 9:38 PM | |
Posts: 6 Rating: (0) |
|
9/5/2016 9:45 PM | |
Posts: 5225 Rating: (1192)
|
Hi. Did you notice that card has errors? I have seen cards like that being damaged by over voltage on the input pins - but it is not to say this is the case for you. Check the voltage and check the hardware configuration (dip switches). Attached is an extract from the System Manual of the S7-200. Good luck. AttachmentExtract_S7-200 System Manual_Analog inputs hardware configure.pdf (413 Downloads) |
This contribution was helpful to2 thankful Users |
Follow us on