Hello, May be it is interesting to check if you comply with the requirements listed here in terms of CPU: What are the requirements for using the S7 routing function and which modules can you implement? http://support.automation.siemens.com/WW/view/en/584459 And for the routing regarding panels, look to here: How do you use WinCC flexible to transfer a project to an operator panel via S7 routing? http://support.automation.siemens.com/WW/view/en/32235096 I wonder also why you only load one CPU with the routing info, and not both. In my opinion you can not route through the DP/DP coupler. The route must always run through a CPU in your case if I understood your configuration correctly. |
Last edited by: jklm at: 1/15/2011 8:35 PMLast edited by: jklm at: 1/15/2011 8:30 PMBest regards |
|