5/12/2017 9:52 AM | |
Posts: 1529 Rating: (202) |
Check your motor cabling The connections MUST be U-U, V-V, W-W. (Drive to motor). |
5/12/2017 10:10 AM | |
Joined: 7/20/2009 Last visit: 1/16/2024 Posts: 61 Rating: (3) |
It is o.k., i have and other power module 3kw and with this works fine! Thanks |
5/12/2017 2:10 PM | |
Joined: 7/20/2009 Last visit: 1/16/2024 Posts: 61 Rating: (3) |
ok... how i can cancer the pole position identification? |
5/12/2017 2:53 PM | |
Joined: 7/20/2009 Last visit: 1/16/2024 Posts: 61 Rating: (3) |
Υou are absolutely right! Works, thank you very much |