10/22/2018 2:23 PM | |
Joined: 1/22/2013 Last visit: 10/13/2022 Posts: 2 Rating: (0) |
Hello. I'm using Axis FB for the vertical axis. During commissioning time I ran into the problem with unexpected movement after axis dataset switching. At those moment Axis FB and Axis were enabled and stopped. After this, I tried switch ADS with disabled FB and Axis. In this case, an unexpected movement didn't happen but arose another problem with status Homed for ADS with the incremental encoder. It goes Off after the second command executePos (or executeMove). In the program, I use three ADS: one with incremental and two with the absolute encoders. Only full-power switching off of D425-2 module helps in this situation. Might anybody have any advice? Regards, Yury ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 10/24/2018 12:27:40 PMNew subject after splitting |
|
10/23/2018 4:06 PM | |
Joined: 10/11/2006 Last visit: 4/19/2024 Posts: 5820 Rating: (787)
|
Hello, Note If the active measuring system is switched via a data set changeover, the _setAndGetEncoderValue() system function should be used to synchronize the two measuring systems before the switchover takes place. This will prevent unwanted compensating movements of the position controller if differences in position are identified General info about data sets: 3.22 Data sets https://support.industry.siemens.com/cs/ww/en/view/109757317 |
With best regards, |
|
This contribution was helpful to1 thankful Users |
10/26/2018 7:24 PM | |
Joined: 1/22/2013 Last visit: 10/13/2022 Posts: 2 Rating: (0) |
Thank you for your quick response. You are right, it should help. I'll fix this problem on the next project trip. |