Joined: 9/27/2006 Last visit: 4/27/2025 Posts: 12347 Rating:
|
Hello Krzychu; This is an extract from the Simatic Net Profibus OLM operations manual, v. 4.0, in the secction concerning the setup of the RS-485 branches on the oprtical ring: http://support.automation.siemens.com/WW/view/en/24164176 In order to minimize disturbances, keep to the following order when connecting an RS-485 bus cable to a PROFIBUS OLM when the network is active: 2. Insert the RS-485 bus connector in the PROFIBUS OLM with a sharp movement and without tilting the connector. Carry out the steps in the reverse order to disconnect a device from the network. Make sure that the bus segment connected to the RS-485 port is terminated at both ends. Only use a connecting cable that is terminated at both ends to connect a single device. If temperatures in excess of 70 °C can occur on the cables or their insertion points or the temperature... |
11/23/2009 9:07 AM | |
Posts: 11 Rating:
|
Hi Everyone Thanks for help:) |