2/4/2020 5:52 PM | |
Posts: 1 Rating: (0) |
I having a problem with the S7-1200 with 4 channel analog output 4-20mA. I have config and test each channel with a multimeter and separately tested the output actuator with an mA simulator. But the error "Short circuit" appeared when I connect more than one actuator to the output module. Also tried with barriers and results are the same, anyone has an idea. Thanks, Bon ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 02/05/2020 11:12:31New subject after splitting |
|
3/27/2020 11:32 AM | |
Joined: 6/19/2019 Last visit: 9/5/2024 Posts: 697 Rating: (73) |
Did you realy connect to these pins — I attached file. The AQ0M contact goes to your load minus and AQ0 contact to your load plus contact? And try re-check your configuration. If this not helped add us your wiring diagram how you connected.Attachments71200_AO.pdf (302 Downloads) |
This contribution was helpful to1 thankful Users |