Hello, I have the same problem with TO objects. we had some problems in Profinet network, and after that "dead" state. Only thing help is to download TO configuration again. I am using GearIn functions. If it works - it works for months, but after 24VDC or profinet problem - complete crash. I tried reset, restart, reset with restart, Enable, EnableAxis, homing, again homing, .... Only thing help is to download TO configuration again or PLC restart, but it is not professional. vacon/danfoss + Leine/Linde encoders need support ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 08/19/2019 09:40:04New subject after splitting |
|
8/19/2019 1:29 PM | |
Joined: 10/11/2006 Last visit: 4/28/2025 Posts: 5990 Rating:
|
Hello, the problem seems to be the error state of the encoder. Contact the manufacturer of the encoder what handshake would be necessary to reset the encoder. It is possible to set or reset Bits of the telegram in Post/Preservo. https://support.industry.siemens.com/cs/ww/en/view/109741575 |