Dear Members, I have a problem configuring WP251 for legal for trade application: as stated in the subject, the problem lies in DR22 (Tolerance parametres) in (Parameter Relation) field OIML restriction is activated in DR3 , therfeore I have 4 choices in DR22 , which are: 1- The tolerance limits are interpreted as percentages of the set point in DS 20 2-The tolerance limits are interpreted as absolute weight values 3-The tolerance limits are calculated based on OIML R61 "Limits of error on verification Class X1". 4-The tolerance limits are calculated based on OIML R61 "Maximum permissible errors in service Class X1". The first three can be sent without problem to WP251, but the last one (underlined) won't be accepted by WP251 and generates a technology message 7062 and 2101 (risk of overfilling). I attached three sceenshots depicting the situation Would you please help me solve the issue. AttachmentDR22 refused wp251.zip (132 Downloads) |
Last edited by: AUTOMATICITY at: 4/28/2017 9:33:02 PM |
|
5/2/2017 11:15 AM | |
Joined: 1/4/2007 Last visit: 12/5/2024 Posts: 1153 Rating: (175)
|
Hello AUTOMATICITY, You have to update your WP251 firmware to version V1.0.1 to avoid this error message: https://support.industry.siemens.com/cs/ww/en/view/109483011 Best regards Siwarexi |
5/4/2017 6:29 AM | |
Joined: 10/29/2016 Last visit: 12/7/2024 Posts: 10 Rating: (1) |
Hi Siwarexi, Problm solved Thanks a lot. 5/5 Best Regards |