7/9/2015 9:14 PM | |
Posts: 34 Rating: (0) |
Hi everyone i'm a beginer and i'm trying to connect wago 750-333 I/O system with CPU 313C-2-DP But I Don't know where i did the mistake i did the same thing like in the wogo manual http://www.wago.com/wagoweb/documentation/app_note/a1008/a100800e.pdf but i got error in the attachement you find what i did in HW and tell me please where i did the mistake i'm sorry if my english not good Attachmentwago.zip (583 Downloads) |
7/9/2015 9:54 PM | |
Joined: 9/27/2006 Last visit: 4/24/2024 Posts: 12257 Rating: (2665) |
Hello karim; Have a look at the Diagnostics section of the 750-333 manual, the first part shows how to evaluate an error based on the diagnostic LED status: http://www.wago.com/wagoweb/documentation/750/eng_manu/coupler_controller/m07500333_xxxxxxxx_0en.pdf By the way, you seem to have no I/O modules setup on the Wago 750-333 Profibus slave; what data exchanges do you plan on transferring to the master? And you seem to have no end module installed to terminate the module bus, ther should always be one (part number 750-600) See the following quote, from the same manual, section 5.5, page 58.
Don't forget the bus end module!
If this is not the issue, one thought that comes to mind is that the Wago module might not have the same address set on the rotary switches that is configured in the S7 Profibus configurator (Profibus address 6). Please check that (there is a section on using these switches for addressing in the manual already mentioned) and come back to us. In any case, there are diagnostic LEDs light up on the S7 Profibus master. The diagnostic buffer of the S7 CPU should contain messages detailing the source of the problem. SF indicates an internal fault, but BF generally means a configured slave cannot be reached (this adds to the possibility of an addressing error). So please open the diagnostic buffer and ry to interpret the errors yous ee there. If you have trouble doing so, Save (As Text) the contents of the buffer and attach the messages that seem to relate to a bus fault to your next reply, we might be able to help you find the source of the problem with more precision. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 7/9/2015 9:56:37 PMLast edited by: dchartier at: 7/9/2015 10:09:03 PM |
|
7/10/2015 3:04 AM | |
Joined: 9/27/2006 Last visit: 4/24/2024 Posts: 12257 Rating: (2665) |
Hllo karim; The firmware (FW) of your 750-333 module is written on the side of the module, along with other data. Select the configuration that is closest to the range of FW in th configuration settings. I believe the following link is the one you showed originally; it contains a sample configuration for the 750-333 as a Profibus slave to a S7-315-2DP master:
Configuration a Profibus-DP node using Step7 and WAGO-I/O components See the attached picture, and the original text for more explanations. By the way, the 750-600 end module is required to terminate the IO bus of the Wago modules, but is not part of the configuration. Hope this helps, Daniel Chartier |
7/10/2015 3:48 AM | |
Posts: 34 Rating: (0) |
Hi dchartier i checked the side of the module but i can't recognize the FW |
7/11/2015 1:00 AM | |
Posts: 34 Rating: (0) |
Hi dchartier thank you a lot for all this helpful informations |
4/10/2016 9:51 PM | |
Joined: 4/21/2006 Last visit: 4/16/2024 Posts: 510 Rating: (24) |
New question published by pharaz is split to a separate thread with the subject wago 750-333?. Best regards |