2/19/2016 2:43 PM | |
Joined: 5/12/2006 Last visit: 11/29/2024 Posts: 22469 Rating: (3033)
|
Hello, please check this FAQ: https://support.industry.siemens.com/cs/ww/en/view/109475049 You have a Panel 2nd Generation and a PLC V1.0 so no communication driver is available. Check the steps for case B from the FAQ. Regards |
Last edited by: ChristophD at: 2/19/2016 2:44:01 PM |
|
This contribution was helpful to1 thankful Users |
2/19/2016 2:54 PM | |
Joined: 6/3/2014 Last visit: 9/26/2024 Posts: 660 Rating: (194) |
Hello JALVIAR, you could also update the firmware of the CPU to 2.X: https://support.industry.siemens.com/cs/ww/de/view/38711660 Then you can connect to the panel the easier standard way (A). |
~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ★ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ |
|
2/19/2016 3:17 PM | |
Joined: 5/12/2006 Last visit: 11/29/2024 Posts: 22469 Rating: (3033)
|
But note that you need a 24MB Memory Card for the FW Update! |