5/5/2011 7:40 AM | |
Posts: 2930 Rating: (432)
|
Hi, where is your program? |
5/5/2011 11:55 AM | |
Posts: 6 Rating: (0) |
Hi Helmut, Please find attached a test program i am running with stated problem Thanks for your help Sean AttachmentWater blowdown.zip (495 Downloads) |
5/10/2011 11:17 AM | |
Posts: 6 Rating: (0) |
Hi schapie, I am using a AC/DC24V LOGO!24RC. The sensor is a burkert flow sensor 8030. The program i upploaded is a testprogram as i wanted to bench test the circuit before i uploaded to the main program. You mentioned that you used an optocoupler...did you use the same power supply unit to feedthe isolated side of the optocoupler into the input on the logo? If so, did you notice any difference in the peak to peak voltage? I am starting to question whether i have a faulty logo as i really cannot see why it is not working. The input voltage stays the same, the only thing that seems to change is the frequency. It would be good to see your solution. Attachmentwater system pressure.zip (423 Downloads) |
Last edited by: Sean969 at: 5/10/2011 12:24 PMAttached is my main program with the frequency counter on input I3 |
|
5/11/2011 4:42 PM | |
Joined: 1/5/2007 Last visit: 4/7/2023 Posts: 1690 Rating: (580)
|
Hi Sean, your LOGO!-type has NO fast frequency inputs - the maximum frequency is 5 Hz !!! Use a other LOGO!-basic module.... OR look under my answer at Water Flow sensor - Counting Pulses HELP! Best regards Betel |
==> Meine TAG-Listen: "deut." |
|