Joined: 2/8/2017 Last visit: 11/28/2022 Posts: 3 Rating: (0) |
I am facing the same problem. Version of GSDML file is corresponding to version of CF firmware. Please help. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 3/18/2019 9:54:30 AMNew subject after splitting |
|
3/18/2019 12:28 PM | |
Joined: 10/11/2006 Last visit: 9/18/2024 Posts: 5906 Rating: (804)
|
Hello, I think there is something wrong with your GSDML... I recommend using the following application example: https://support.industry.siemens.com/cs/ww/en/view/92022677 With the help of the script from the link above, you can automatically generate your telegram specific GSDML file and afterwards you can install it in TIA Portal. 1st: Configure the drive in STARTER and select all telegrams that you will use 2nd: Import the script to your project 3rd: run the script, (the original GSD file of your firmware can be found here:https://support.industry.siemens.com/cs/ww/en/view/49217480) 4th: finish the script, install the generated GSD file in TIA Portal 5th: replace the GSD in Devices & networks in TIA 6th: configure the IP address & the profinet name of the GSD (compare it with your S120 that you can find online under Online access -> search for accessible nodes) I hope that it will work for you, please let me know if you need any further assistance. |
With best regards, |
|