Hello All, Is there any sheet availablewhich provides all the "PII"(Process Image Input) and "PIO"(Process Image output) Sizes for all the ET200M modules . |
6/10/2013 10:44 AM | |
Posts: 1547 Rating:
|
Hello, the Process image in general will be no problem. For PROFIBUS the maximum data size for communication to Master will be 240 Bytes. The first limit will be the maximum amount of modulesetc. is more important. You will find this information in technical data of the ET200-M itself. SIMATIC Distributed I/O device ET200M This information is also within GSD file to give the configuration software the possibility to check the configuration limits. Step 7 will check this information during save and compile. I suggest adding your configuration into Step7 HW-Config and save and compile to let the software check the configuration. If you don't have Step7 you can use the ET200 Configurator |