10/9/2009 10:58 AM | |
Posts: 325 Rating: (14) |
Hi All, Could any one let me know how PCS7 decides the number of Process Objects used for a user defined FB in a PCS7 project. Regards Nil |
10/10/2009 9:07 AM | |
Joined: 4/5/2006 Last visit: 11/28/2024 Posts: 917 Rating: (63) |
Hi Nil96 , in addition what Phantom75said, during comparation of PO used from Simatic Manager Statics and WinCC PO/Tag used you'll see the number is not same. Until PCS7 v7 each block generating message on WinCC occupy 1 PO, and every 25 Tags will be one more PO; from PCS7 v7.1 every 50 Tags will be counted one more PO. I asket time ago to Tecnichal support and thats has been the answer, but I didn't found documentation yet about this question, sorry Regards |
10/13/2009 11:17 AM | |
Joined: 4/5/2006 Last visit: 11/28/2024 Posts: 917 Rating: (63) |
Hi Nil96 , you right untill you check PO used by Simatic Manager....not same for WinCC. Often happens you check in simatic Manager for a certain number of used PO, then compile OS, to dicovers the WinCC PO changed (always greater ). WinCC count PO in different way: WinCC count all tags / 50 = 1 PO, as well as explained in catalog (in attachment for v7.0), then get the greater value between PO coming from Simatic Manager and WinCC counting. Hope can help Regard |