Dear Saeed, The handbook for the SINEC L2 interface of the S5-95U is described in the manual SINEC L2 Interface of the S5-95U Programmable Controller In STEP7 you may place a SIMATIC S5 station with a Profibus FDL interface. Then it is possible to give the SSAP and DSAP addresses, but please consider that the 95U have SAP-addresses that are forgiven when you have choosen the bus-address, see the handbook. Please also consider the timing of the network, this because you are not working with one package, but with STEP7 and STEP5! There the S5-95U is not so fast as the CP 342-5 you have to choose the timing of the 95U also for the CP 342-5. The timing is also mentioned in the manual. You need COM DB1 to program the interface, this package is delivered with and called fromSTEP5. |
I hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|