Hi all who can tell me know what the Profibus telegrams when S7 300 PLC communication with HMI via Profibus ex. SD? SSAP DSAP ? DU?... anybody help me?
AttachmentProfibus.pdf (297 Downloads) |
Last edited by: danhsistech at: 1/22/2013 3:42 PM |
|
1/24/2013 9:10 AM | |
Joined: 10/7/2005 Last visit: 3/17/2025 Posts: 3042 Rating:
|
Hello danhsistech as Daniel already said, when the Class 2 master HMI has the token, it willsend it's request as a - well let's say - "general" Profibus DP telegram to the PLC. In thiscase it is an SD2 type DP telegram (= telegram with variable information and lenght) as the SD type value is68hex (first byte in telegram and explained in the pdf that you had attached to your first post). What a Siemens HMI does though is to use the S7 protocol to talk to the S7 PLC and this is a Siemens proprietary protocoland you won't find the makeup of the DU (data unit) explained in the Profibus Standards (FC, SSAP and DSAP are outside of the ProfibusDP defined ones too and Siemens specific). While I'm not to sure why you want to decipher the S7 protocol (sheer curiousity perhaps?), you will find some info on it with Google search. I hope this helps |
Last edited by: fritz at: 1/24/2013 9:11 AMCheers |
|
This contribution was helpful to
1 thankful Users |
1/25/2013 5:42 AM | |
Joined: 12/15/2011 Last visit: 3/15/2024 Posts: 11 Rating:
|
hi dchartier I use a cable RS232 - RS485 and a software "Eltima Serial Port"
|