Hello Sandeep, Redundant CPU communication over profibus is not yet possible directly. You have to convert redundant DP port to standard one using Y link modules. is youn configure y-link in your system then you can now use G120 as with standard non redundant CPU. This application example describes steps for configuring profibus communication. Hope this helps. Kbv. |