Hello baghram; I agree withthe preceeding comments fromSte39, Umencho and eisenpferdreiter. Just to add a standard document to support what we are stating, you should download the Profibus Installation Guidelines from Profibus International (it is the 6th link in the table): http://www.profibus.com/download/installation-guide/ From that link there are a few documewnts you can look at, start with the PROFIBUS Installation Guideline for Planning, from which I have extracted the attached illustration. It shows that the standard topology for Profibus copper cables is linear, or what we call daisy-chained. You seem to want to use a star connection, and this is not supported. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 7/22/2014 6:38 PMLast edited by: dchartier at: 7/22/2014 5:59 PM |
|
This contribution was helpful to
1 thankful Users |
7/23/2014 7:08 AM | |
Joined: 10/7/2005 Last visit: 3/20/2025 Posts: 3042 Rating:
|
Hello bhagwan12345 buy a ProfiHub B5from your nearest PROCENTEC Distributor and Bob's your uncle as they say. |