7/28/2013 9:46 AM | |
Posts: 22 Rating:
|
Hi all Is it possible to establish PROFIBUS connection between PLC S7 300 and OP37? Thanks |
7/28/2013 10:22 AM | |
Posts: 8946 Rating:
|
If your OP37 has a MPI/DP interface you can connect it. But I counseling to go for a new panle because OP37 has finished for a couple of years already. |
7/28/2013 10:38 AM | |
Posts: 22 Rating:
|
Thanks for reply yes It has MPI/DP interface but in STEP7 there is not OP37 for choose. how can I connect them? |
7/28/2013 5:19 PM | |
Joined: 9/27/2006 Last visit: 3/23/2025 Posts: 12344 Rating:
|
Hello sahar; When you use Profibus-DP to exchange between a Siemens OP and a Siemens PLC, the OP is a master class 2 on Profibus-DP, not a Profibus-DP slave. That is why you cannot "select" an OP37 (or any other OP/TP/MP module) in the PLC's Profibus configuration. The communication must be setup on the OP37 software. I have found these documents for the OP37 and Protool,together they should guide you properly for this Profibus interface: ProTool Configuration Software Communication |
This contribution was helpful to
2 thankful Users |