2/19/2019 4:28 PM | |
Joined: 9/27/2006 Last visit: 6/1/2023 Posts: 12030 Rating:
|
Hello Thompson; Hati's answer is spot on. Profibus-DP normally uses daisy-chain connectivity, as shown in the very primitive drawing below. Whenever you introduce a T-junction (like your connectivity box) to design a star topology, you must considered the T-junction as the end of a segment, each branch as a start of a new segment, ant the terminators must be active entering and exiting the connectivity box. At lower transmission speeds and small lengths of bus, RS-485 (Profibus--DP, in this case) can be tolerant of some termination issues, which is probably why this installation worked without problems for some time. However, the first time a termination issue appeared, you lost the consistency of the network and you find out that your topology is not as robust as you thought.Now termination issues appear and you lose different stations in different branches. So, as Hati requested earlier, what exactly did you use for the connectivity box? Could you consider changing it for a RS-485 repeater, with which you could establish your star network, or redoing the Profibus cabling to return to the standard daisy-chain structure? RS-485 repeater manual: https://support.industry.siemens.com/cs/ww/en/view/48598071 Hope thia helps, Daniel Chartier |
Last edited by: dchartier at: 2/19/2019 4:29:35 PM |
|
This contribution was helpful to
1 thankful Users |