Hello, Terminating resistor is ON at both ends in order to avoid signal reflection. |
Eng.Mohamed Ibrahim |
|
This contribution was helpful to
1 thankful Users |
6/8/2015 6:38 AM | |
Joined: 10/7/2005 Last visit: 3/23/2025 Posts: 3042 Rating:
|
Hello Nklai
Please check how long the cable is between the OLM and the CP342-5. While the advise by Online tech is of course correct and each Segment mus be terminated on either end, there can be situations where this could make it worse rather than improve the situation. The general rule is that you should always have at least 1m of Profibus cable between two neighbouring stations (be that station a DP Master, DP Slave, OLM, repeater etc.). This 1m of cable decouples the two stations from each other so that the capacitive mismatch each station creates does NOT add up and creates undue reflections. This 1m rule will also hopefully one day soon make it into the official Profibus guidelines. If you have only two stations on a Segment though (as is the case here), you are best adviced to have at least 2m of cable installed between the two. If not (and assuming both terminators are on as they normally should be), you can end up "over terminating" the Segment which may the reason someone decided to NOT have the terminator on at the CP342-5 (and while this 2m rule is generally accepted best practice, you won't find it in any official documentation). I hope this helps |