5/12/2011 10:25 AM | |
Joined: 10/7/2005 Last visit: 4/23/2025 Posts: 3047 Rating:
|
Hello automation_1 in addition to Wizard's advise, you could also ask Danfoss why they don't support 45.45 kbps. You may find that the answer is perhpas as simple as"well, wedidn't think about this speed as it is a bit of special DP speed needed only to accomodate the Siemens PA couplers". If that's the case, either get them to change their GSD fileOR do it yourself by adding the line 45.45_supp = 1 to it and see if the Drive accepts it (add after the line that states "19.2_supp = 1").
|
Cheers |
|
5/12/2011 2:33 PM | |
Posts: 133 Rating:
|
great fritz! changing GSD file it seems to work, thank you |